Hi guys, just fired up a new BL2840 on 12/31/14, going trough 75' of logster into the basement then going into 1' copper. Problem is I have 190 on the auquastat and not over 160 on 2 guages in the basement. Getting a air noise in the pipes and pump, Taco 0010, I have an automatic air eleminator installed and have turned ball valves on and off since fired up, still think I have air in the lines. Does anyone have any suggestions on how to get air out of the lines? I have also been told it just takes time, maybe it will come out of the fill spout on the boiler. Thanks for the input.
-
Filling the boiler through the underground lines, first on supply then on returns will eliminate any air pockets by pushing that air to the boiler and venting out the top
-
Slimjim, I have the same problem with my pump since I started it three weeks ago. The pump always has air in it. What would you suggest to get it out ?
-
Did you fill the boiler from the lines or through the top of the boiler?
-
From the inside fill line Slim
-
Did you fill the supply line with the return valve shut off?
-
NO :-[
-
Close the return first and backfill through the supply, note the check valve must be removed from the circ first
-
The boiler is full right to the full line already. There is no air vents on the system because it is an open system.
-
Yes but with air in the supply line the circ will not push air back to the boiler, it will eventually kill your circ as air will get trapped there
-
Slim I think im just confused about what your suggesting to do ? I really don't want to kill a new 26-99
-
Give me a call!
-
Ok thanks
-
I just installed a spirovent jr down on the feed coming out of oil boiler feed to upstairs air handler no more bubbles noise or air so far it's so quiet down by the circulating pumps can't tell if there working,the fact is the hotter the water the more oxygen and gas will be given off in the system and this keeps it out of the system.i have a open direct plumbed system and never had a issue till I bumped the temp up to 192 for the high cut off. So on a closed system I guess install next to heat x changer before it,they say where the water hotter follow directions.
-
5050, I only have one question why do you have an Air Eliminator (SpiroVent JR) on an open loop system?? I have only every seen them installed in closed loop (Pressurized) systems, to help get rid of TINY dissolved bubbles
-
As u heat any water air will come out so before it gets raised to the 2nd floor hot water coil to eliminate any air that my want to come out of solution before it goes up to attic n get trapped up there,I don't have a bleeder in attic removed it cause without the pressure it was wanting to let air in, my circulater pump runs all the time to it,that's how u keep the water up there without getting air in it it works great for 2 years now no heat exchanger open system works for me