Finally after 2 years I have in slab heat in my garage.....sorta...
I have a Tekmar 519 with slab sensor going to a Taco SR501, Problem is, that the wiring pics from tekmar doesn't jive with the switching relay...help??
Thanks
Mike
-
Can you post their schematic?
-
ill try, but at work
-
see the schematics
-
I figured it out....what was confusing me was the 24v and the com wire into the switching relay as shown on the tek pic. What I needed to do was C to Com(which was labeled as 24vav/com on the taco switching relay) R to Rh, W to W1, and put a jumper from R to Rh in the t-stat.
Initially I wanted the slab to be set at 55, but 65 is much nicer :) but we shall see about the consumption.