I have a boiler that I hooked up to another building last year and am ready to run it to the house. Problem: I popped off the side of the plenum of my late '80's Williamson highboy and there is no room between the A coil and the top of the plenum before it heads down the horizontal distribution.

So does that mean I need to replace the furnace before tackling the boiler? It is a 350' run from boiler so I am already looking at the expense of the Thermopex. I am guessing I will need to put in a new furnace which these days are much smaller footprint for the btu. Then postpone the boiler run for a few years.

Old furnace so the upgrade is worthy but defeats the purpose of going to a woodboiler.

Hate to just run the 50KBTU secondary building with a CL6048. So much overkill.
Title: Re: No room for heat exchanger
Post by: RSI on August 27, 2017, 11:34:40 AM
Is there anywhere on the return side of the furnace that you can mount a heat exchanger? A furnace that old should not have anything in it that would be affected by the heat like some newer ones might.

If you are going 350' each way, I would not use 1" Thermopex. You will want pipe that is at least a full 1" ID.
Title: Re: No room for heat exchanger
Post by: mlappin on August 27, 2017, 12:47:04 PM
Can you go under the A coil? If not then like been suggested, place it in the return duct and let the furnace pull air thru it.
Title: Re: No room for heat exchanger
Post by: shepherd boy on August 27, 2017, 02:59:51 PM
 Can you lift the a-coil to give room under the a-coil for the water coil? You can lift an a-coil up into the horizontal duck if need be. If it is to the top of the horizontal duck your out of luck on supply side.
Title: Re: No room for heat exchanger
Post by: mlappin on August 27, 2017, 04:58:50 PM
I have a guy that will raise the a-coil for 50 bucks, I could do it myself, but he’s  a AC guy anyways, if he screws it up he can fix it.

Prefer it on the heat side of the furnace if at all possible, then the furnace can back feed heat to the boiler if required.
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 27, 2017, 07:29:28 PM
Mr. Lappin and I have discussed the size before. I had a local dealer spec 1" Thermopex/Rahu. I called Central Boiler and the VP even said 1" unless there was slope involved. And he recommended the Taco Viridian pump.

Inlet is available but the size would be considerably smaller exchanger than the outlet. Top of acoil is almost to top of box. I might be able to squeeze the exchanger below it but my understanding is the exchanger always goes last and not closer than 12" due to chance of freezing.


Title: Re: No room for heat exchanger
Post by: Gunpowder on August 27, 2017, 07:39:19 PM
Can you go under the A coil? If not then like been suggested, place it in the return duct and let the furnace pull air thru it.

I know if it goes within 12" above ther is a chance of freezing. But you can install it directly underneath? I always read it has to go abover the A Coil.
Title: Re: No room for heat exchanger
Post by: Smokeless on August 27, 2017, 08:38:01 PM
Go with the Logstor full 1" inside dia. 1 deg heat loss /100'  It will pay for itself many times over.
Cost of electricity is more pumping water threw smaller pipe. 
We explain this several times a year on this sight.
Use a grundfos 26-99. 3 speed. Shoulder months run on Med. then when it gets cold switch to hi.
Title: Re: No room for heat exchanger
Post by: mlappin on August 27, 2017, 10:51:04 PM
Can you go under the A coil? If not then like been suggested, place it in the return duct and let the furnace pull air thru it.

 I always read it has to go abover the A Coil.

Why?

Order on mine is HX then a coil, but I have a bastardized setup, like four foot of duct between HX and A coil. Don’t ask, a bunch of free stuff my tin knocker Dad brought home from work years ago.

I could see where you wouldn’t want the A coil practically sitting on the HX, the drip tray could cause weird air flow patterns thru the HX.

Title: Re: No room for heat exchanger
Post by: E Yoder on August 28, 2017, 02:42:37 AM
Coils in the return are quite common, probably will work better starting and stopping flow to prevent convection up the cold air return.
If you want it to backfeed heat then you'll have to lift the AC coil or use two coils on the duct branches.
You could route the yellow wire to the compressor through a freeze protector sensor if you're concerned about freezing.
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 28, 2017, 07:36:39 AM
Go with the Logstor full 1" inside dia. 1 deg heat loss /100'  It will pay for itself many times over.
Cost of electricity is more pumping water threw smaller pipe. 
We explain this several times a year on this sight.
Use a grundfos 26-99. 3 speed. Shoulder months run on Med. then when it gets cold switch to hi.

The new Taco Viridian pump is suppose to be 80% less electricity to run. Central Boiler said make sure to use it because of the cost benefits to use vs the older models.

Logstor is the only manufacturer of true 1" ID aren't they? I assume it is close to the 1" Thermopex vs 1 1/4?
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 28, 2017, 09:34:17 AM
I might have room to raise the A Coil. there is about 5" above it to the top of the Plenum and 2" below it ti the base of the furnace box. That would be preferred to putting it in the return where the HX would have to be so tiny to fit. 
Title: Re: No room for heat exchanger
Post by: shepherd boy on August 28, 2017, 09:41:24 AM
 Just wondering the logic of why a coil will freeze if it's within 12" of the ac coil? Does the air warm that much in 12"? I've put a number of them within 1" above with on problem.

  Yes, raise it 4". That will give you 6". I've done many tight against but you'll have several inches for air space. I'd rather do that than in the return in an oil or gas furnace.
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 29, 2017, 12:58:14 PM
I contacted another dealer who said 1" Logstar should work on my 350' run. Anyone have a link to an online calculator to look at the 3/4 (Thermopex) 1" (Logstar) and 1 1/4 (Logstor) calculations?

According to my math w/o just use of a calcualtor, at 350' and assuming 20 DT and a 100,000 BTU furnace (furnace is 100,000, HX is est 200,000 BTU). I used 100,000 in calculation.

1" Logstor  (using 1" pex table)= 43.89 head?
1 1/4 Logstor (Using 1 1/4 pex table)= 15.63 head?
Title: Re: No room for heat exchanger
Post by: E Yoder on August 29, 2017, 02:39:51 PM
I don't have Taco Viridian specs in front of me but the only way I'd think you'd get 100,000 btu's with that medium head pump on 1" is by running a large(ish) (like 40 degrees) delta T.
 The coil is oversized it sounds so it might work? At low flow you'd want to counterflow the coil. Obviously 1 1/4" would flow much easier.
That's just an estimate..
Title: Re: No room for heat exchanger
Post by: RSI on August 29, 2017, 10:49:43 PM
I contacted another dealer who said 1" Logstar should work on my 350' run. Anyone have a link to an online calculator to look at the 3/4 (Thermopex) 1" (Logstar) and 1 1/4 (Logstor) calculations?

According to my math w/o just use of a calcualtor, at 350' and assuming 20 DT and a 100,000 BTU furnace (furnace is 100,000, HX is est 200,000 BTU). I used 100,000 in calculation.

1" Logstor  (using 1" pex table)= 43.89 head?
1 1/4 Logstor (Using 1 1/4 pex table)= 15.63 head?
What GPM are you using for these numbers? If you figure just the 350' of pipe at 10 GPM the 1" Logstor would be about 34.5' of head and 1-1/4" Logstor would be 11.75' of head. (logstor 1-1/4" is not anything close in size to standard 1-1/4" pex)
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 30, 2017, 11:27:03 AM
I used 10 GPM
1"
KxCxLx(F 1.75)
.00223 x 1.0 x 350 x 56.234 = 43.89

1 1/4

.000794 x 1 x 350 x 56.234 = 15.63

Obviously Logstor is metric but close enough.

Taco VR1618 specs:

 operating modes:
- Fixed speed (     ) - infinitely adjustable min/max settings
- Constant pressure (   ), variable speed - 3 constant pressure differential curves (5, 10, or 15 feet of head)
- Proportional pressure (   ), variable speed - 3 variable pressure differential curves (High, Med, or Low
    Maximum Shut-off Head: 18 feet 
  •     Maximum Flow: 16 gpm
  •     Maximum Operating Pressure:
125 psi 
(8.6 bar)
  •     Maximum Water Temp: 230°F (110°C)
  •     Minimum Water Temp: 36°F (2°C)
  •     Electrical specifications:
Voltage: 120V, 60 Hz 
Single phase
Operating Power: 4W - 44W
Max. AMP Rating: 0.54
  •    Equipped with a cast iron casing     
and should be used for closed
loop systems only
  •     Taco circulator pumps are   
for indoor use only
  •     Acceptable for use with water or     
maximum of 50% water/glycol solution
Title: Re: No room for heat exchanger
Post by: mlappin on August 30, 2017, 11:33:31 AM
Even with 11 feet of head, the Viridian won’t move 10gpm, least not according to the chart.

http://www.taco-hvac.com/uploads/FileLibrary/102-499.pdf

A Grundfos 26-99 on Med will though.

http://s3.supplyhouse.com/manuals/1297872762860/47830_PROD_FILE.pdf
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 30, 2017, 12:12:36 PM
Even with 11 feet of head, the Viridian won’t move 10gpm, least not according to the chart.

http://www.taco-hvac.com/uploads/FileLibrary/102-499.pdf

A Grundfos 26-99 on Med will though.

http://s3.supplyhouse.com/manuals/1297872762860/47830_PROD_FILE.pdf

Yep. Is my math still right? Approx 44 head with 1" pex? Not sure the numbers to use for 1" Logstor though. I used basic 1" pex numbers off a chart.

At $6,300 for 1 1/4 Logstor or $4,865 for 1" logstor, that's a might big sandwich to eat. I can put a high efficiency furnace in for less than that. Total cost one could put in a Geo system. The CL6048 is already set up on the 50KBTU other building. that is way overkill boiler for that demand on its own. Grrr
Title: Re: No room for heat exchanger
Post by: mlappin on August 30, 2017, 01:41:54 PM
Even with 11 feet of head, the Viridian won’t move 10gpm, least not according to the chart.

http://www.taco-hvac.com/uploads/FileLibrary/102-499.pdf

A Grundfos 26-99 on Med will though.

http://s3.supplyhouse.com/manuals/1297872762860/47830_PROD_FILE.pdf

Yep. Is my math still right? Approx 44 head with 1" pex? Not sure the numbers to use for 1" Logstor though. I used basic 1" pex numbers off a chart.

At $6,300 for 1 1/4 Logstor or $4,865 for 1" logstor, that's a might big sandwich to eat. I can put a high efficiency furnace in for less than that. Total cost one could put in a Geo system. The CL6048 is already set up on the 50KBTU other building. that is way overkill boiler for that demand on its own. Grrr

Im sure Logstor has its own numbers to use, use the numbers for copper and you’ll be close enough for guvmint work.

Other pipes are available, I like Logstor, but you could get 1 1/4” Performaflex Ultra from Z supply for roughly two bucks a foot less than 1” Logstor. Could always have one pump pushing to the house then another pump pushing back to the stove.
Title: Re: No room for heat exchanger
Post by: Gunpowder on August 30, 2017, 02:12:02 PM
I want to stay with dense foam like Logstor/thermopex/Reheau for the obvious benefits.
Title: Re: No room for heat exchanger
Post by: aarmga on August 30, 2017, 08:24:21 PM
I was just contemplating with 44 head feet that pump is going to be working pretty hard.  I'd go with the 1-1/4" for sure.  But at that price plus install plus the stove why not go with a geo system?  Can be done for under 20 Grand now and rebates available.  Plus you don't have to worry about cutting wood or replacing your furnace.
Title: Re: No room for heat exchanger
Post by: Gunpowder on September 14, 2017, 01:38:03 PM
To put closure on this thread. I successfully raised my a-coil 6" so I have room for a HX. Assuming I get approval from the board tonight (monthly board meeting for the nonprofit), I plan to install 1.26” (32mm I.D.) Logstore which is about same I.D. size as the 1 1/4 thermapox. Head should be under 17 so a Grundfos 26-99FC will work.
Title: Re: No room for heat exchanger
Post by: slimjim on September 14, 2017, 02:05:37 PM
Best of luck at your meeting!
Title: Re: No room for heat exchanger
Post by: Gunpowder on September 14, 2017, 02:19:00 PM
Best of luck at your meeting!

The CB 6048 is already installed and 75' of Thermapex ran to the office/nature center. The run in question is to my residence so I am the mercy of the board as I pay my own utilities. Looks like a little over $5K will install the pex and HX plus plumbing. That's a big chunk for a nonprofit these days.