Re: Furnace/Heat won't shut off.
« Reply #15 on: February 07, 2013, 08:23:22 PM »

Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #16 on: February 07, 2013, 08:31:53 PM »

Unhooking wires from zone valve wouldn't shut the fan off, there is something shorted out and sending power to the zone valve and fan

Remove the green wire from the thermostat and see what happens
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

loneryder

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #17 on: February 07, 2013, 08:53:31 PM »

Unhooking wires from zone valve wouldn't shut the fan off, there is something shorted out and sending power to the zone valve and fan

Remove the green wire from the thermostat and see what happens
I removed the green wire from the G terminal on the tstat and it's still running?????
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Furnace/Heat won't shut off.
« Reply #18 on: February 07, 2013, 08:54:23 PM »

Try at the furnace end. If it is a short it could be after the thermostat.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #19 on: February 07, 2013, 09:01:07 PM »

Gettin closer, hope this tells him something

If it thinks the heat strips are on it may not shut down for a minute or two later
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

loneryder

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #20 on: February 07, 2013, 09:38:25 PM »

Gettin closer, hope this tells him something

If it thinks the heat strips are on it may not shut down for a minute or two later

No strips aren't on.  Where is the G wire in the furnace? I had the front panel off and didn't see anything obvious.  The tstat wires seem to be connected to a lot of wires with wire nuts.
Logged

loneryder

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #21 on: February 07, 2013, 09:49:28 PM »

I'm at a loss.  Hopefully I can get someone out tomorrow to look at it.  All the weird unexplainable crap happens to me. 
Thanks for everyone's help.
Logged

loneryder

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Furnace/Heat won't shut off.
« Reply #22 on: February 08, 2013, 08:43:33 AM »

OK so I talk to my owb dealer and he suggested tapping on all the relays.  The big one is the fan delay relay and 2 smallerr ones the installer put in.  Fan started cycling normally.  I've located a new fan relay for $15 so will install that and see if it stays working.  Dealer said once they get hung up like that, they will usually go bad.  It must have been a coincidence that it happened when I opened that zone valve.  crap like that always happens to me so why can't I win the lottery?? :)
Thanks for everyones suggestions.