Author Topic: CB - E-Classic 2400 - Temp Setting and "Back Draft"  (Read 5366 times)

Ken01

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 7
  • OWF Brand: Central Boiler
  • OWF Model: E-2400
    • View Profile
CB - E-Classic 2400 - Temp Setting and "Back Draft"
« on: April 12, 2012, 12:46:43 PM »

New to the Forum, but it seem informative based on what I have read so far

Ran a Classic 6048 for 5 years and this past year converted to an E-Classic 2400.  Have two questions if anyone has a thought.   1)  Digital temp reading on FireStarter Control Panel is 15 degrees warmer then water coming out of furnace - this seems odd to me.  CB dealer change the control panel and the difference increased to 20 degrees.  Have tested the water at the water level check value on the back of the furnace and on a in-line thermometer I have.  With the 6048 I had a 2 degree differential but now a 15 degree.    I have to run my high set point at 190+ degrees to keep the water in the furnace at 175 degrees.  Is this  normal ???      2)  on the E-classic the air blower is in the back with three solenoids opening air flows.  On occasion I find the air blower / solenoid area has been "back drafted" with a grey ash.  Can not figure out what set of conditions cause this "back draft" to occur nor have I ever seen or heard it happen.  Anyone else experienced this?
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: CB - E-Classic 2400 - Temp Setting and "Back Draft"
« Reply #1 on: April 12, 2012, 06:52:41 PM »

ken just wondering why you gave up the 6048? this was my 2nd winter with mine and cant imagine there is a better owb gaser or not
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

boilerman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 270
  • OWF Brand: Central Boiler
  • OWF Model: E2400 Currently CL5648 Previously
    • View Profile
Re: CB - E-Classic 2400 - Temp Setting and "Back Draft"
« Reply #2 on: April 12, 2012, 11:18:14 PM »

Ken, I would confirm that you do not have a pump reversed. Check the flow direction arrow on it, or check your owners manual to be certain your supply/return lines are not hooked up backwards or into the wrong ports. A 15-20 degee difference sounds like you may be pulling off the bottom and returning to the top of the water jacket in the rear corner above the pump mounting area, while your Firestar controller is reading from the top front right. That would be the only explanation I can think of.

Regarding backdraft dust into air intake box, I think I have had that happen if I let my coalbed get to deep in the firebox so it does not draw down like it should.
Logged

Ken01

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 7
  • OWF Brand: Central Boiler
  • OWF Model: E-2400
    • View Profile
Re: CB - E-Classic 2400 - Temp Setting and "Back Draft"
« Reply #3 on: April 13, 2012, 04:11:54 AM »

ken just wondering why you gave up the 6048? this was my 2nd winter with mine and cant imagine there is a better owb gaser or not

Converted from the 6048 due to neighbors concerns about smoke.  The E-2400 smokes a lot less and is using less wood over all.   I loved the 6048 and it worked well.   If it wasn't for the smoke / neighbor issue I would still have it.
Logged

Ken01

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 7
  • OWF Brand: Central Boiler
  • OWF Model: E-2400
    • View Profile
Re: CB - E-Classic 2400 - Temp Setting and "Back Draft"
« Reply #4 on: April 13, 2012, 04:16:11 AM »

Ken, I would confirm that you do not have a pump reversed. Check the flow direction arrow on it, or check your owners manual to be certain your supply/return lines are not hooked up backwards or into the wrong ports. A 15-20 degee difference sounds like you may be pulling off the bottom and returning to the top of the water jacket in the rear corner above the pump mounting area, while your Firestar controller is reading from the top front right. That would be the only explanation I can think of.

Regarding backdraft dust into air intake box, I think I have had that happen if I let my coalbed get to deep in the firebox so it does not draw down like it should.

Good suggestion to check the water flow.  I believe it is right but I may just reverse the pump and see if that changes temp. 

I will keep an eye on my coal bed and see if that has an effect on the backdraft dust.   I try to let it burn down before adding wood but my schedule does not always allow it so could be on those days when I add wood to soon this is happening.   Thanks for the thoughts.
Logged

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: CB - E-Classic 2400 - Temp Setting and "Back Draft"
« Reply #5 on: April 13, 2012, 02:17:52 PM »

Ken, I would confirm that you do not have a pump reversed. Check the flow direction arrow on it, or check your owners manual to be certain your supply/return lines are not hooked up backwards or into the wrong ports. A 15-20 degee difference sounds like you may be pulling off the bottom and returning to the top of the water jacket in the rear corner above the pump mounting area, while your Firestar controller is reading from the top front right. That would be the only explanation I can think of.

Regarding backdraft dust into air intake box, I think I have had that happen if I let my coalbed get to deep in the firebox so it does not draw down like it should.

Good suggestion to check the water flow.  I believe it is right but I may just reverse the pump and see if that changes temp. 

I will keep an eye on my coal bed and see if that has an effect on the backdraft dust.   I try to let it burn down before adding wood but my schedule does not always allow it so could be on those days when I add wood to soon this is happening.   Thanks for the thoughts.

Ken,  For my E1400, the manual says to wait at least 15 seconds before closing the by pass door after stoking the fire box.  If you do it sooner, smoke and creosote may gather in the primary solenoid and air box area.  Roger
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire