More about operating temps
« on: March 23, 2013, 11:42:35 AM »

Natures Comfort just added a new part to there warranty, which shows they to are seeing the importance of keeping firebox temps up.  They likely haven't gotten to the part of return temps being as important, but I suspect they'll be looking at some type of thermostatic valve soon as well

This is from the mew warranty.

The Nature's Comfort 20 Year Limited Warranty

Nature's Comfort LLC, of Shipshewana, IN 46565 warrants material and labor on any defects in workmanship on the fire drum for a period of 20 years from the purchase date to the original owner only (see proration below). The water jacket is warranted for a period of 10 years from the purchase date to the original owner only (see proration below). If there is a leak in your properly delivered, installed and maintained Nature's Comfort boiler, we will cover repair costs for the first 5 years and prorated after that (see below).  Repair can be denied if the unit's water jacket has exceeded 220 degrees. The aquastat must be set so the water jacket temperature never falls below 150F otherwise condensation will be created on the inside of the firebox and will cause corrosion that is not covered under warranty.
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

WoodMOJoe

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 312
  • OWF Brand: Homemade Tank-in-Tank Furnace
  • OWF Model: Ol' Fireball #0002
    • View Profile
Re: More about operating temps
« Reply #1 on: March 23, 2013, 02:46:40 PM »

Interesting.  Is there a positive way of knowing...or proving what temps an aquastat has been set to?
Logged
Southwest Missouri Ozarks...USA

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: More about operating temps
« Reply #2 on: March 23, 2013, 07:09:35 PM »

Nope.... 

I also wanna see someone get a stove 220 degrees, water won't get that hot unless its under pressure. 

The thing is though how would anyone know where they had kept the aquastat set at?  Loopholes loopholes

That's why I say it's important to have a good install and hopefully a dealer that has some leverage if a problem should arise
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: More about operating temps
« Reply #3 on: March 23, 2013, 07:51:48 PM »

I guess the furnace could easily hit 220 if you ran it without water in it?
Logged
Southwest Virginia
WF4000 Heat Master

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: More about operating temps
« Reply #4 on: March 23, 2013, 09:05:57 PM »

I guess the furnace could easily hit 220 if you ran it without water in it?

Oh yea no doubt... 

It says if the water jacket has exceeded 220 degrees..  Who would know how hot the water jacket had gotten?  I mean that's as clear as muddy water. 

Same way with the aquastat settings?  You could simply say, you operated the stove to cold and the discussion be over.  Only way to ensure they couldn't adjust things to dangerous levels is to have them pre set with pass codes, then there is still the factor of folks adding more things and killing return temps, that's where the thermo valves will come into play
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

victor6deep

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 393
  • OWF Brand: Burnrite
  • OWF Model: 228
    • View Profile
Re: More about operating temps
« Reply #5 on: March 24, 2013, 02:41:55 PM »

So a setting of 150-160 can be used.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: More about operating temps
« Reply #6 on: March 24, 2013, 03:18:05 PM »

No

If your at 150 with a delta t of 20-30 degrees your return temps are going to be to cold

I was just showing that all companies are starting to notice the importance of it, it won't be long until you see that line in the warranty change to "boiler protection required" or "thermostatic valve required"

It takes the industry a while to catch up, cb has been doing this a while, empyre started last year requiring it, p and m, and several others have been offering them to customers and are in process of requiring these
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: More about operating temps
« Reply #7 on: March 24, 2013, 03:23:06 PM »

It wasn't long ago we had a discussion on here about a failed p and m, we found out at the farm show that customer had return temps of 105-115 degrees

Victor, if you set it at 150-160 and knew ur delta t could get no larger than 10, which is hard to do, I guess u could run it at those temps.  But why?  You have said yourself the firebox stayed cleaner and seemed to be more efficient at higher temps, another factor is the dissolved oxygen content in the water itself, the higher the temp up to like 175 is the lower the o2 content. 

I just don't see why it's wanted to run that 150 temp vs 180 when there is virtually nothing positive to come out of it. 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: More about operating temps
« Reply #8 on: March 24, 2013, 04:48:52 PM »

Its like your gonna save any wood..The boiler is gonna work just as hard if was set at 150F vs 180F..Why not keep the temps up..
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: More about operating temps
« Reply #9 on: March 24, 2013, 05:00:03 PM »

Matt, when you have long underground pipe runs you save energy when you run lower temps.  Even when using quality insulated pipe it makes a difference. I did a service call on a furnace today that has over 400ft of pipe in the ground going to multiple buildings, on runs like that you see a difference. If you are running 50ft to a house its not that big a deal.
Logged
Southwest Virginia
WF4000 Heat Master

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: More about operating temps
« Reply #10 on: March 24, 2013, 05:02:01 PM »

Its like your gonna save any wood..The boiler is gonna work just as hard if was set at 150F vs 180F..Why not keep the temps up..

It beats me...  I've ran them both ways in the past and I can't say for certain if 180 uses more than 150, if it does it's not noticeable to me.  It sure doesn't change the btu demands of your home, that's for sure
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: More about operating temps
« Reply #11 on: March 24, 2013, 05:07:14 PM »

Its like your gonna save any wood..The boiler is gonna work just as hard if was set at 150F vs 180F..Why not keep the temps up..

It beats me...  I've ran them both ways in the past and I can't say for certain if 180 uses more than 150, if it does it's not noticeable to me.  It sure doesn't change the btu demands of your home, that's for sure

the savings of lower temps in the underground pipes will be a lower delta (the difference of the ground temp to the pipes temp.) if your water in the pipes is 180 and the ground is 50 there will more heat loss to the ground than if the water in the pipes was 160 and the ground temp was still 50, the difference in a short run as stated will not be much..in longer runs it would be more. but also as scott says you need to keep those return temps up too
Logged
home made OWB (2012)
Ontario Canada

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: More about operating temps
« Reply #12 on: March 24, 2013, 05:54:11 PM »

Matt, when you have long underground pipe runs you save energy when you run lower temps.  Even when using quality insulated pipe it makes a difference. I did a service call on a furnace today that has over 400ft of pipe in the ground going to multiple buildings, on runs like that you see a difference. If you are running 50ft to a house its not that big a deal.
How could you heat mulit building's with lower temps?? Esp in the dead of winter with wind chill factors ect..  I would think the wood boiler would never shut off..
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: More about operating temps
« Reply #13 on: March 24, 2013, 06:13:45 PM »

depending on insulation value  lets say you have  2000 square foot home that has 6 ich bats in your walls and cieling and good windows..you may need 40,000 btu per hour to heat that home on teh worst night of the year (just a number)  that would be 4 gpm at 180 degrees or you might say that 10 gpm at 160 degrees. (again just a number) could deliver the same amount of btu per hour

it is a largely accepted number(in the heating world) that 1 gpm of 180 degree water can deliver 10,000 btu of heat..so if you lowered the  temp of the water you would need to increase the flow to get the same amount of btu to the home.
Logged
home made OWB (2012)
Ontario Canada

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: More about operating temps
« Reply #14 on: March 24, 2013, 06:25:41 PM »

Many of my customers change the setting depending on the weather. Most would not be running a furnace at 150 when its really cold out. I normally drop mine down to 150 when it gets above 40 and you only need a little heat. I normally run mine at 180 during the coldest part of winter. Like I said before, I'm sure there is a huge difference between furnaces made of mild steel or furnaces without ash pans and stainless furnaces with ash pans. I can't speak for the former because Heat Master only makes stainless furnaces including the gassifiers. 
Logged