Author Topic: Initial return temps.  (Read 13792 times)
ST98
« on: October 13, 2013, 05:49:17 PM »
I've seen lots of posts about the importance of return temps being in the 20 degree or less range. I'm not sure if that means in the initial call for heat.
 When I put a load on my furnace I watch the temps on the side of the furnace. With no load it goes out at 185 and comes back at 183. Wether it's the 50' run or the 175' both one way. When I put a load on my return drops to around 100 or so in a minute and then climbs back up to maybe 170 in a minute or so.  Then stays within 20 degrees difference or less for the duration.  It seems that initial slug of cool water cools her down. I put heat exchangers sizes in as recommended.  Everything else cycles fine.  These reading are coming off the valves I installed on the furnace for out and return. The water sensor on the furnace might go down from 185 to 184.
Is this ok?
jerkash
  • OWF Brand: Legend
Re: Initial return temps.
« Reply #1 on: October 13, 2013, 07:17:17 PM »
Do your pumps run continuous?
ST98
« Reply #2 on: October 13, 2013, 07:24:21 PM »
Yes. 50' run 26-99 set on medium or high.
« Reply #3 on: October 13, 2013, 07:55:52 PM »
Your fine, it would be bad though if your returns stayed crazy low, but if its an initial drop and then it climbs back I think you'd be fine
ST98
« Reply #4 on: October 14, 2013, 04:12:18 AM »
Did I plumb my HE correctly. 4 standard 1 1/4 ports reduced to 1 inch.
Upper right comes in from OWB, supply
Lower right goes back to OWB, return
Upper left goes to heating units, supply
Lower right is the return from those units, return
« Reply #5 on: October 14, 2013, 07:22:32 AM »
Yea it sounds fine!
ST98
« Reply #6 on: October 14, 2013, 04:56:42 PM »
Scott, are you saying the he sounds fine or the return temps?
Is this normal or did I do something wrong?
« Reply #7 on: October 14, 2013, 06:36:30 PM »
Yes it's plumbed right.  Not much difference there as long as sides are proper.
In regards to temp drop.  If its only initially I wouldn't worry much
ST98
« Reply #8 on: October 15, 2013, 04:52:56 PM »
Thanks. I'd like to get along time out of this boiler and wanted to start on the right foot.
Thanks again
chillyhiker
  • OWF Brand: Ridgewood from scott7m
  • OWF Model: 6000
« Reply #9 on: October 15, 2013, 07:39:56 PM »
If your stove is set at say 180...do you really need a temp gauge on the outbound line?...I would think you could just put it  on the return line.. or cant you trust the Ranco or other auquastat?....just thnkin.
stihl chain saws
husky spliter
 trailer for haulin wood.
« Reply #10 on: October 16, 2013, 04:57:45 AM »
Temp guages can and should be placed on the lines as the boiler aquastat is typically mounted on the upper side of the boiler and may not be an accurate reading of the water temp coming out of the boiler in the rear.
ST98
« Reply #11 on: October 16, 2013, 10:06:21 AM »
I put them on all lines at the furnace. Honeywell gauges were like 10 or 15 bucks a piece. The outgoing temps and incoming temps are pretty much the same but the boiler reads a lower temp.
ST98
« Reply #12 on: October 20, 2013, 04:39:40 AM »
One more question about return temps. If I have a thermostatic valve that is set at 155 and the cold slug of water goes through does it activate and shut my supply water off?  How would I ever get warm water through?
« Reply #13 on: October 20, 2013, 05:19:08 AM »
Your thermistic valve should be simply mixing hot water with the return water to bring up return temps, it should not stop flow to the building completly
ST98
« Reply #14 on: October 20, 2013, 02:03:11 PM »
I wasn't sure how it worked and thought I may have been over thinking it a bit.