side arm hot water exchanger....
« on: November 16, 2013, 06:13:16 PM »

I am going to make a side arm heat exchanger for my electric hot water heater out of stainless steel....I can get scraps from my buddy that works for a company that makes maple products, evap. and so on....I was going to take a 2 inch pipe or 3 inch pipe about 24 inch or 36 inch long,drill 2 holes in the side of it....one at the top on the side for boiler hot in and one on the bottom on the side for boiler water to go out with one inch pipe, threaded on ends to except 1inch female pex fitting with barbed end..........then run 1 inch threw center for hot water heater water to run threw with 1 inch threded ends as well.....like the copper ones you can buy just out stainless steel..... I can do all the work in my own fab shop.....I can tig weld it all together and cut threads in 1 inch pipe and so on....what do you think? It will last a long time this way and wont have anything it except time..... :)
kelly
Logged
husqvarna 357 xp
allis-chalmers 5050 2,100 org hrs
farmall m (set up for just tractor pulling)
farmall H

idahohay

  • Guest
Re: side arm hot water exchanger....
« Reply #1 on: November 16, 2013, 06:24:42 PM »

I hope you go ahead with it and post some pictures. I plan to make one myself but out of copper and brass. I acquired some 2" coper pipe, and will attempt to spin a copper 2" x 3/4" reducer on a wood lathe. So your idea is alot more sane than mine.
Logged

baldwin racing

  • Full Member
  • ***
  • Offline Offline
  • Posts: 210
  • OWF Brand: Thermo-Control (indoor)
  • OWF Model: 500/2000 (in the insulated jacket)
    • View Profile
Re: side arm hot water exchanger....
« Reply #2 on: November 16, 2013, 06:34:11 PM »

I hope you go ahead with it and post some pictures. I plan to make one myself but out of copper and brass. I acquired some 2" coper pipe, and will attempt to spin a copper 2" x 3/4" reducer on a wood lathe. So your idea is alot more sane than mine.

hey worth a try.......you want to use mine....lol
I must have hit the button twice sorry same pic.....lol
kelly
« Last Edit: November 16, 2013, 06:35:45 PM by baldwin racing »
Logged
husqvarna 357 xp
allis-chalmers 5050 2,100 org hrs
farmall m (set up for just tractor pulling)
farmall H

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: side arm hot water exchanger....
« Reply #3 on: November 16, 2013, 07:11:54 PM »

hey boys you guys sound pretty handy why not make your own tube and shell or coil in a shell and have absolute unlimited hot water (like a palte exchanger) and have little to almost no added head pressure

iused a 50 foot coil f soft 1/2 inch copper (domestic water supply) and coiled it inside a 12 inch pipe that the OWB water goes through...very little restriction (head pressure) and all the "on demand" hot water you could ever want
Logged
home made OWB (2012)
Ontario Canada

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: side arm hot water exchanger....
« Reply #4 on: November 16, 2013, 07:53:51 PM »

I am going to make a side arm heat exchanger for my electric hot water heater out of stainless steel....I can get scraps from my buddy that works for a company that makes maple products, evap. and so on....I was going to take a 2 inch pipe or 3 inch pipe about 24 inch or 36 inch long,drill 2 holes in the side of it....one at the top on the side for boiler hot in and one on the bottom on the side for boiler water to go out with one inch pipe, threaded on ends to except 1inch female pex fitting with barbed end..........then run 1 inch threw center for hot water heater water to run threw with 1 inch threded ends as well.....like the copper ones you can buy just out stainless steel..... I can do all the work in my own fab shop.....I can tig weld it all together and cut threads in 1 inch pipe and so on....what do you think? It will last a long time this way and wont have anything it except time..... :)
kelly

It should work but stainless will have less heat transfer than copper and the copper sidearms with just a single 3/4" pipe through the center don't have very good heat transfer. If you make it, go with as much heat transfer surface as possible.

You can buy pre-made stainless steel sidearms for around $175 so I would try to keep cost well below that.
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: side arm hot water exchanger....
« Reply #5 on: November 16, 2013, 07:55:42 PM »

I hope you go ahead with it and post some pictures. I plan to make one myself but out of copper and brass. I acquired some 2" coper pipe, and will attempt to spin a copper 2" x 3/4" reducer on a wood lathe. So your idea is alot more sane than mine.
Wouldn't it be easier to just buy a 2" to 3/4" copper reducer fitting?
Logged

idahohay

  • Guest
Re: side arm hot water exchanger....
« Reply #6 on: November 16, 2013, 08:55:06 PM »

RSI, no doubt easier to buy a couple or just buy the sidearm but have been experimenting with metal spinning anyway.

kelly, thats a sweet little metal lathe.
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: side arm hot water exchanger....
« Reply #7 on: November 16, 2013, 10:16:03 PM »

I have no idea how hard it is to do that. I sounded like a lot of work to save a couple $7 fittings.

Are you able to close the end on 1/4" ID copper? I have been looking for a source for making cheap thermowells and haven't been able to find anything.
Logged

idahohay

  • Guest
Re: side arm hot water exchanger....
« Reply #8 on: November 16, 2013, 11:46:58 PM »

Not sure how a thermowell is made, probably couldn't do it.
Logged

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: side arm hot water exchanger....
« Reply #9 on: November 17, 2013, 05:44:38 AM »

What is the reason you decided to use a side arm instead of a flat plate? I've always wondered why people still use them.
Logged
Southwest Virginia
WF4000 Heat Master

idahohay

  • Guest
Re: side arm hot water exchanger....
« Reply #10 on: November 17, 2013, 07:37:00 AM »

Since my hot water needs are low and quick recovery isn't an issue, I'm using a sidearm. My thinking is it will add the least amount of head to my system and the use of the lowest possible wattage circulator. Along with the FPHE itself,  there is usually  all the extra fittings, valves, y-strainer, etc.  But if I still had kids at home and a high demand for hot water, for sure a flat plate.
Logged

martyinmi

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 541
  • OWF Brand: Portage and Main
  • OWF Model: Optimizer 250
    • View Profile
Re: side arm hot water exchanger....
« Reply #11 on: November 17, 2013, 12:14:18 PM »

What is the reason you decided to use a side arm instead of a flat plate? I've always wondered why people still use them.
I guess the reason that I'm still not a big fan of plate exchangers is the huge amount of heat they can pull out of boiler water. My buddy has a 30 plate that will pull 30 plus degrees out of his water when his shower and washing machine are both in use(he does not have a tempering valve installed, so even with the washer set on warm,it will scald!).
His water to air exchanger will sometimes pull up to an additional 25 degrees out when the house calls for heat.
He runs his boiler temps quite high-190 on and 195 off, but he has still seen return temperatures at his boiler 135 degree range.

We use a sidearm mounted to our old(installed in the '60's) Bradford White 52 gallon water heater. Throughout the winter we may run out of hot water a half dozen times or so, and if we need a quick recovery, I just flip the breaker and 20 minutes later we have hot water.
I plumbed a mixing valve(anti-scald) in, so my water heater thinks it is much bigger than it actually is, so running out is seldom a concern.

I probably over think things sometimes, but having higher return temperatures by using a sidearm should increase the longevity of my boiler. There have been times when I've not put enough wood in and came out to a boiler with a temperature of less than 180*. Both my exchangers will not lower my water temperature more than 30*, so I rarely hit the 140* temps that we are warned against dropping down to.

Just a few thoughts from an old farmboy. ;)
Logged
Newholland TZ-25da
30+ Chain Saws
'05 Dodge Diesel
Michigander
TSC 35 Ton Splitter

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: side arm hot water exchanger....
« Reply #12 on: November 17, 2013, 01:42:02 PM »

Marty, why is he running a 30?  With such huge deltas it seems he has some really low flow
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: side arm hot water exchanger....
« Reply #13 on: November 17, 2013, 03:25:29 PM »

 I have to agree with Scott, proper sizing would help. And how often is the flat plate being used? Not often, maybe at the most 5% of the total time. Don't base your return temps on that.
Logged
Southwest Virginia
WF4000 Heat Master

martyinmi

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 541
  • OWF Brand: Portage and Main
  • OWF Model: Optimizer 250
    • View Profile
Re: side arm hot water exchanger....
« Reply #14 on: November 17, 2013, 03:49:02 PM »

Scott,
He is running the 3 speed Grundfos (15-58?) on the high setting.
Isn't a 25 - 30 drop fairly normal for a Chinese made 30?
Oh, and he's running a 30 because he bought used off the net, shipped to his house for under 80 bucks...I think?
And...he's cheap!

He has about the same change temperature through his furnace exchanger (25* plus or minus a few as I do), so I'm thinking his flow is OK...???

I threw the 135 degree temperature out there just to remind folks that their boiler temps shouldn't be allowed to get that low. To my knowledge, his boiler never has, only the return line temperature. The occasional low return line water temperature, even that low, shouldn't ever have any bearing on condensation forming in the fire box as long as the actual boiler temperature is much higher.
Logged