Pulled the trigger on a P&M BL 2840, now I'm figuring out the materials for the rest of the install. I've followed the Taco Pump Sizing Guide from other threads and it doesn't seem to be adding up right. Can someone check my math here and give some input?
First my setup.....OWB will be about 90 feet from the house so call it 100 with turn up into the stove and house (no basement so have to turn up through the wall). I will have approximately 25' of pex one way to the DWH plate exchanger and heat exchanger coil in the plenum. My house is about 3200 sqft and according to a manual J done by my HVAC guy has about a 90,000 btu load.
Given all of this I have calculated my target flow rate to be 9 gpm with a 20 deg Dt. With that flow rate, it looks like I need to be running an 1.25" pex. Estimating my total circuit to be 275' multiplied by a factor of 1.5 to estimate additional pressure loss due to fittings, valves, etc. (as given in this article from another thread
http://www.fueloilnews.com/ME2/dirmod.asp?nm=&type=MultiPublishing&mod=PublishingTitles&mid=8F3A7027421841978F18BE895F87F791&tier=4&id=663F2C7F5BA543968C4AAB1732E86FFB ), I come up with a head loss of 14'. I come up to a Taco 0014.
This seems large to me given that I've seen a lot of guys on here running 1" pex and 008 & 009's. I know every application is different but just want to get some input from some of you more knowledgeable guys.
I had originally planned on running 1" pex until now. What would the downside be to this?
Also I'm thinking about going with a variable speed delta t pump. How would this affect the pump size calculated above?
Thank for any input given guys!