Ok, I am totally a believer in the lower input temperatures sent into the floor!  It really works.  I have went all weekend running a 100 degree SWT, and at the beginning of a cycle, the RWT is right around 77-78 degrees.  It takes quite awhile, maybe 30-45 minutes, but the RWT will rise to about 80 to maybe 81 degrees and sit there for some time before the wall thermostat is satisfied at a 72 degree set point.   I will continue to play with the Supply water temp, running it down slightly more to see what it will do with the return temps.  I need to purchase an infra-red thermometer to check floor surface temps.  
The biggest problem I am facing now is the fact that once my wall thermostat is satisfied, and shuts the circulating pump off, my living space is so tight, that such a long period of time may pass before the wall thermostat calls for heat again, and in the mean time, I am loosing my fire in the OWB.  Hardy H2, I have removed both screws from the blower flap, I have turned the aquastat up to 175 set point.  In the past couple of weeks, I have come home from work to absolutely no fire in the box, having to unload and re-start a fire.  This is VERY frustrating.  I am simply not getting enough burn cycles during the middle of the day, allowing the fire to burn out.  Some may say this is a good problem, but really, it sucks.  This is an issue that I do not know how to overcome.  Maybe it will be better since I have lowered the SWT, creating a more constant cooler RWT to the boiler, therefore creating a few more burn cycles throughout the day.  Yesterday, being Sunday, I found the Wall Thermostat at 72 degrees, pump off, and about 4 hours later, it was 73 degrees in the house.  I ended up opening windows to get some cool air in the house (yesterdays high was about 39 or 40).  This is my year #2 and I'm still learning as I go!