All-Purpose OWF Discussions => General Outdoor Furnace Discussion => Topic started by: gainerspot on October 03, 2014, 12:20:13 AM
-
Can I T off from my logstor and run one line to DHW and the other to the Water to Air exchange, or does it need to be a single loop?
I have been using this formula to figure the head loss. I cant seem to come up with any info on how to calculate for the heat exchanges. Any info on this would be helpful.
http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf (http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf)
-
A drawing or sketch would really help...
If you were using a FPHE, I would definately recommend put it in as a secondary loop, as they can have very high head pressures.
Since water to air exchangers have less restrictions you may be able to put in primary loop, but I have never installed a water to air exchanger, so...
-
I have a 20 plate DHW flat plate and a 60 plate exchanger inline and no problems. I did install valves and bypass for problems or maintenance. On the 20 plate I leave the bypass valve partially open so some bypass can happen and prevent back pressure.
-
Yes you can that how I have mine, just put a valve in the line to the dhw so you can control the flow between the two.
-
Can I T off from my logstor and run one line to DHW and the other to the Water to Air exchange, or does it need to be a single loop?
I have been using this formula to figure the head loss. I cant seem to come up with any info on how to calculate for the heat exchanges. Any info on this would be helpful.
http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf (http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf)
That will only work if you have a pump on each run.