Advice/assistance on hook er' up!!!
« on: September 19, 2011, 06:11:15 AM »

Built first fire @9pm last night!! 

P&M Opt 250.  Got plenty of condensation from the fresh filling of 55 deg well water.  Understandable, I suppose.
This morning finds it drying out, with none in the fire box, and just some stains left on the concrete.  Deem that event Normal!
Can make one wonder, "Where's the leak"???  Next...

Set controller for 170 set and on at 160.  70 plate W-W HX in basement.  Fed by Taco 008 pump.  50 some feet of the Logstor buried and 35 feet of 1" oxygen barrier pex inside.  Got to 170 at OWB and only see 150 deg going into propane boiler.
  *****   The propane boiler still fires when a zone calls for heat???  So, for now, shut switch of on propane boiler. 
All zones still work.   Advice?  Thanx in advance...

I cut in a tee off top of propane boiler and went to common return pipe from all zones.  Installed clapper type check valve on this line couple inches off of tee.  Common return line now goes to 70 plate WWHX.  Return from HX to propane boiler with taco 007 pump at lowest point, after HX,  running continously.   2nd floor tstats shut down, but still hit 70deg?  Menopausel wife had rough nights sleep!! (gave her my side of bed near window!!)
    *****   I think maybe flowing through zones, even though check valve installed correctly??? 

High note....7 pcs of split got her up to temp and 2 pcs this morning to keep fire in box!  Looks like its out when idling!  No smoke!  Did smoke a bit on initial firing, but smooth right out when started gassifying.  Of course it was night when built fire, but didn't look bad at all.

Did add 1/2 pale of ashes from old wood stove in basement to floor of new OWB, as hot fire right on new floor don't seem too good.

        Thanks for reading, look forward to thoughts/replys.

        Bill G
Logged
Bill
Stihl saws
Homegrown splitter
'10 3500 Dodge Cummins
(Beagles and snowshoe hares!!)
NE PA

Ridgekid

  • Guest
Re: Advice/assistance on hook er' up!!!
« Reply #1 on: September 19, 2011, 06:33:24 AM »

You did it! Impressed!

Stain on concrete? From door gasket? When I first fired mine up I had alot of moisture also, from sweating I presume. Sound like the same?

No smoke? Sounds like mine when it's at idle.

Not sure about the rest of your install. Are you heating your HWH first? Plate HX or sidearm? Could you be loosing 20F there? Not sure, just guessing.

Is this just a test run or are you on line for the winter? I'm on heat mode (heatpump) as the high temps have been chilly. But not cold enough to fire up the CB.

Don't forget those pics!
Logged

Bill G

  • Full Member
  • ***
  • Offline Offline
  • Posts: 166
  • OWF Brand: Portage and Main
  • OWF Model: Opt. 250
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #2 on: September 19, 2011, 07:15:14 AM »

Good morning, Ridgekid!!!

First time in years, I said "should have fire by Sunday" and hit the mark even if it was 9 pm!

Yeah, condensation from all of the HX tubes and fire box.  Well water was cold!  All good there this morning, just some streaks and stains from it running down here and there.  Will give "shine job" shortly!

Loosing 20 deg some how?  Comes in from OWB, bottom of HX return from top.  From "Ol money eater" Propane boiler, off top, Tee to common return pipe (1" copper)  Straight through tee feeds zones when called.  5 zones return vertical to that horizontal common return.  I have a clapper type check valve right off this tee.  So, when a zone pump calls, the return pressure from that zone's pump  should close check/clapper valve and go through HX.  When there is no call for heat, the "cont. on" pump should pull through HX, push into bottom of propane boiler, out top and through check/clapper valve.

I suppose I better consult with the good plumber who installed this system when we built this house, back in 2000.  He's good about such stuff and will be able to hopefully offer up some thoughts/solutions.  In the mean time, I'm all ears from you guys!!!  Thanks much!

My friends think my basement near propane boiler looks like a picture of the boiler room on a submarine!  Quite busy looking but neatly done.  Just some bugs to work through.

Jr. is in school, so pic's impossible til' afternoon.

Sorry for my poor narrative description of my system. 

Thinking maybe should try upping OWB to 180deg off 170 on?  Maybe this temp will satisfy propane boiler, so it don't fire when a zone calls for heat?  But, the 20deg drop don't seem to right?

Bill
Logged
Bill
Stihl saws
Homegrown splitter
'10 3500 Dodge Cummins
(Beagles and snowshoe hares!!)
NE PA

kjw58

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 79
  • OWF Brand: Natures Comfort
  • OWF Model: 275G- Coal Burner
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #3 on: September 19, 2011, 08:07:43 AM »

Hi Bill G
 I don't know about you plumbing issues, but you will find that your gassifier will work much better if you run it at a higher temp.  When the refractory stone stays hotter the stove will begin gassifying much faster and will actually burn less wood.  I don't have the same model you do but have seen one in use and it was very impressive.   :thumbup:
Logged
S.E. Mich.
New Holland TC40DA
IH 464 w/2250 Loader
6 x 10 Dump Trailer
2 Stihl 261's
Poulan 3400 & 3700
Poulan 2150
Homelite Super XL

Ridgekid

  • Guest
Re: Advice/assistance on hook er' up!!!
« Reply #4 on: September 19, 2011, 08:08:50 AM »

BiilG-

I don't want to add to the confusion as I'm not familiar with Propane boilers. But here's my concept of your setup.

Your using the OWB to heat the water in the Propane bolier, is that right? Which means the OWB pump is continually flowing hotwater, through your 70 plate HX. Your propane boiler has it's own pump circulating the water through your zones when called for? Does the pump on the propane boiler only kick on when it calls for heat? Or do you have a third pump thats circulating water from the 70 plate to keep the propane water hot?

Another dumb question- On your 70 plate, if mounted vertical one side (top and bottom is to the OWB and the other side is Propane boiler right? (When I first got my 20 plate it was not clear how to set up as I thought both ports on top was one system and the bottom was the other-which would of been wrong) And the two systems are crossing flowing? (Does the OWB water go in bottom and come out top and propane boiler go in top and come out bottom?)  Again I apologize if this was obvious to you, just passing on what I learned after I recieved my 20 plate.

How about the DHWX? do you have one? (or sidearm?)

I may not have contributed anything here, but it is a learning expierance for me.

EDIT: One more thing- I added pipe wrap around all my pex in the basement. Pretty cheap investment and makes the install look better.
« Last Edit: September 19, 2011, 08:22:50 AM by Ridgekid »
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Advice/assistance on hook er' up!!!
« Reply #5 on: September 19, 2011, 03:56:25 PM »

To keep the propane boiler from firing, I would just use a strap on aquastat it turn off the propane boiler when the pipes on the OWB side of the plate are hot.
You will get a 10-20° lower temperature on the secondary side of the plate. The only way to get it closer is going bigger. Even if you went up to a 100 plate it would probably be a few degrees hotter but still likely won't get to the same temp.
Logged

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #6 on: September 19, 2011, 04:05:06 PM »

most all heat/cooling gurus say 20 degree between feed and return is acceptable

your taco 08 pump curve is (depending on the head pressure) 0- 15 gpm your target flow should be the middle of the chart. that puts you at about 6 gpm at 12 foot head. (if head is less gpm is more) if you were to upgrade to a larger pump (say a taco 11) your pump curve would be between 0-31 gpm and your target area to be near the middle of the chart would be 16 gpm at 17 foot head. if you were to deliver 10 gpm to your exchanger at 170 degrees you would be delivering about 100,000 btu per hour and i do believe in hot water systems this is a good target. perhaps your 08 is delivering this now? if yoru water temp is lower you need more gpm.

you dont want a pump that is too large either..i would (if you can) see how many gpm you are delivering to your exchanger now and see if you think you need to improve that or not. i mean if the 08 is working, why change it but it would be nice to know what your pump is delivering so if you burn out the one you have you will have a beter idea on what to replace it with
« Last Edit: September 19, 2011, 04:30:26 PM by willieG »
Logged
home made OWB (2012)
Ontario Canada

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Advice/assistance on hook er' up!!!
« Reply #7 on: September 19, 2011, 04:38:35 PM »

What is the temperature or the OWB coming out of the plate? You won't be able to get the indoor loop hotter than that. If it is dropping the then a bigger pump will help.

WillieG, just curious what reasons you have not to go with a bigger pump? The only thing I can think of is waste of power.
Logged

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #8 on: September 19, 2011, 05:06:43 PM »

waste of power mostly  but i have also been told (no confirmation yet) that a non pressure sytem with air mixed in the water, can, with a too large of pump cause the pump too (as pressur builds from the pumps push on the line going out) to actually start to seperate the air from the water in the pump and cause cavitation. this may be BS but if i ever find out the truth i will pass it on. i could not desput the fact as i don't know and this came from a pump guy. he said in pressurized systems it wont happen as the pressure is about the same all through the system so pressure on each side of the pump is always within a few psi,  but in our systems the pressure could be so great as there will be none on the suction side and depending on head pressure we could have a great amount in teh pump that could lead to cavitation? what would your thought s on this be rsi ? more opinions are good food for thought and if anyone has proof one way of the other is even better.
Logged
home made OWB (2012)
Ontario Canada

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Advice/assistance on hook er' up!!!
« Reply #9 on: September 19, 2011, 05:36:02 PM »

Air mixed in the water is bad for any pump. It should eventually all make it's way to the boiler and out the top.

I have found that Grundfos pumps are a lot more tolerant of air than Taco. That is one of the reasons I would never sell a Taco.

I hope there isn't any truth to that because I will be running a B&G PL36 pump this winter. (supposed to use a lot less power but I will see  ;D)
The flow curve is from 40GPM to 40FT of head.
I have about 120' of Kitec each way to the house and 3 heat exchangers on a manifold setup (4 when the dryer is running) so there shouldn't be that much head pressure.
Logged

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #10 on: September 19, 2011, 05:50:16 PM »

im not sure i belileve the whole idea but i guess it may be possable but i think you would have to have a lot of small bore pipe in the main lines...that is why he says to aim for a pump that will be in the middle of its pump curve. i always try to aim for the 10gpm area. there is somewhere between 10,000 and 11,000 btu per hour, per gpm at 170 to 180 degrees F.  so if we maintain the area of 10 gpm we are delivering 100,000 btu per hour or better and that should heat any home and if i can do that in the middle of a pumps curve..the pump is running in it's most efficient zone and cost to run that pump in this zone is the best it can be
Logged
home made OWB (2012)
Ontario Canada

martyinmi

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 541
  • OWF Brand: Portage and Main
  • OWF Model: Optimizer 250
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #11 on: September 19, 2011, 06:02:11 PM »

Built first fire @9pm last night!! 

P&M Opt 250.  Got plenty of condensation from the fresh filling of 55 deg well water.  Understandable, I suppose.
This morning finds it drying out, with none in the fire box, and just some stains left on the concrete.  Deem that event Normal!
Can make one wonder, "Where's the leak"???  Next...

Set controller for 170 set and on at 160.  70 plate W-W HX in basement.  Fed by Taco 008 pump.  50 some feet of the Logstor buried and 35 feet of 1" oxygen barrier pex inside.  Got to 170 at OWB and only see 150 deg going into propane boiler.
  *****   The propane boiler still fires when a zone calls for heat???  So, for now, shut switch of on propane boiler. 
All zones still work.   Advice?  Thanx in advance...

I cut in a tee off top of propane boiler and went to common return pipe from all zones.  Installed clapper type check valve on this line couple inches off of tee.  Common return line now goes to 70 plate WWHX.  Return from HX to propane boiler with taco 007 pump at lowest point, after HX,  running continously.   2nd floor tstats shut down, but still hit 70deg?  Menopausel wife had rough nights sleep!! (gave her my side of bed near window!!)
    *****   I think maybe flowing through zones, even though check valve installed correctly??? 

High note....7 pcs of split got her up to temp and 2 pcs this morning to keep fire in box!  Looks like its out when idling!  No smoke!  Did smoke a bit on initial firing, but smooth right out when started gassifying.  Of course it was night when built fire, but didn't look bad at all.

Did add 1/2 pale of ashes from old wood stove in basement to floor of new OWB, as hot fire right on new floor don't seem too good.

        Thanks for reading, look forward to thoughts/replys.

        Bill G
The condensation is normal- all three of our 250's leaked like mad from the back door, and some from the front. Our's all started gasifing within an hour or so, mine a little sooner as I have experience with gassers. You are going to love that thing. One of the first things you'll notice is the different smell from the exhaust when it's gasifying- it smells way different that a conventional OWB. Sort of like comparing an older diesel to todays modern electronic ones. Mine's been burning a little more than a week now and I can't say enough good about it. I hear all the horror stories from others(different mfgs.) trying to keep theirs lit when the weather is a little warmer, but I've not had any issues yet. Keeping the boiler temperature up is also very important as you will figure out. We set ours all at 180* right out of the gate. Do yourself a favor and try not to pull too much heat out of the water, as they've found out return temps under 150* can do harm(condensation) to the combustion chamber.
   Keep us updated. Congrats! I may be a little biased, but I think you own the best brand out there.
Logged
Newholland TZ-25da
30+ Chain Saws
'05 Dodge Diesel
Michigander
TSC 35 Ton Splitter

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Advice/assistance on hook er' up!!!
« Reply #12 on: September 19, 2011, 06:24:29 PM »

im not sure i belileve the whole idea but i guess it may be possable but i think you would have to have a lot of small bore pipe in the main lines...that is why he says to aim for a pump that will be in the middle of its pump curve. i always try to aim for the 10gpm area. there is somewhere between 10,000 and 11,000 btu per hour, per gpm at 170 to 180 degrees F.  so if we maintain the area of 10 gpm we are delivering 100,000 btu per hour or better and that should heat any home and if i can do that in the middle of a pumps curve..the pump is running in it's most efficient zone and cost to run that pump in this zone is the best it can be
Actually the temperature of the water has nothing to do with the BTU's it is the GPM and temperature drop that does. If you have 180 degree water and you pull it down to 170 you are getting the exact same btu's transferred as if it was 150 degrees and you pull it down to 140 degrees. Of course you would need larger heat exchangers to pull the same btu's out of the water at the lower temperature though.

You need to know the headloss of your system to get a pump in the middle and that is a lot more complicated than most people will be able to figure out. Using a larger 3 speed pump if the easiest way to do it. Just put on high and see what happens when going to a lower setting.
Logged

Bill G

  • Full Member
  • ***
  • Offline Offline
  • Posts: 166
  • OWF Brand: Portage and Main
  • OWF Model: Opt. 250
    • View Profile
Re: Advice/assistance on hook er' up!!!
« Reply #13 on: September 19, 2011, 06:29:37 PM »

Thanks Guys,

Ridge, I did plumb HX correct, Bot in top out from owb.  Propane...top in bot out.  I did the make sure whilst admiring my handy works today.

I'll be going up to 180 off and 170 on when I get my system straigtened out.  If current loss of 20 deg is what I can expect, a buck60 deg in water will surely heat my house and hot water.

     In betweenst putting tools away and clean up, I come up with this possible problem.....There is 5    007 Taco pumps  1 for each zone  (4 heat and 1 Dom hot water)   Mounted verticle to horizontal common return to propane boiler.  I cut this Com Return away from propane boiler,use to go in bottom, and put it into a tee from top of propane boiler.  Also put in flow check valve and FP ball valve.  Then other side of common return now goes to top of HX.  Out bottom with a 007 pump running cont. to bottom of propane boiler.

     I think, (and that's painful for me)  that with out flow checks between zone pumps and common return, that it must be back feeding through zones.   And I need some kind of controlled valve in place of the check valve that I installed off of main top outlet of boiler.  So when no zones are calling for heat, the water just circles through common return, HX, cont on pump, in bot of boiler and out top, up to the tee, but can't continue on up through house.  Goes left back into common return. 

     Is a 3 way valve what I need, and how would it get hooked/wired to the five zone circulators?  In my not so infinate wisdom, I figured the pressure of off discharge side of the zone pump would close the clapper/check valve I installed and go out the other side of common return through HX.  Maybe just the installation of check valves under the zone pumps will cure my problem?

     Sorry for the amateur sounding post, but I's trying!  Appreciate the assistance! 

Bill

Said I have 3 new replys as I was typing, so I'll post and read the 3 above this...
Logged
Bill
Stihl saws
Homegrown splitter
'10 3500 Dodge Cummins
(Beagles and snowshoe hares!!)
NE PA

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Advice/assistance on hook er' up!!!
« Reply #14 on: September 19, 2011, 06:33:23 PM »

Can you post a picture or diagram of your setup?