More attic insulation vs. Adding hx/air to attic unit
« on: October 03, 2011, 09:22:29 AM »

Any opinions on the which investment you would do first please.

My home was built in 2008. Basement (unfinished) 1250 sq ft, main level 1250 sq ft, second level 1250 sq ft.

The main level and second level have separate Carrier heat systems. I have a HeatMasterSS MF5000E interfaced with the main level Carrier system.

The main level is heated via hx/air along with hx/water for hot water. I set the thermostat on 71 degrees and the main level stays comfortable. However, the second level, which has an open staircase, does not seem to get any heat from the main level and stays about 64 to 65 degrees in moderate outside temperatures. 

I just wonder if that is what most would typically expect.

The attic has typical insulation between the framework of the second level ceiling, there is no blown-in insulation.

Would it be a better investment to get insulation blown-in to the attic, or would it just be more beneficial to add another hx/air to the attic heating system?

Thanks in advance!

Michael

Logged
HeatMasterSS MF5000E by Yoder Heating
MS 460 Stihl Magnum
Husqvarna 345
8lb Wood Splitter with 'High Performance' Fiberglass Handle
5 acres

jerkash

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 280
  • OWF Brand: Legend
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #1 on: October 03, 2011, 01:29:47 PM »

I would cut a hole in the ceiling of your mail level/floor of the top level and install a grate/vent.
I have a friend that did this and he heated his upstairs completely from the downstairs unit.
Logged

mcarter

  • Full Member
  • ***
  • Offline Offline
  • Posts: 100
  • OWF Brand: HeatMasterSS
  • OWF Model: MF5000e
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #2 on: October 03, 2011, 02:53:52 PM »

With the open staircase to the second level, I sort of already have that type of setup. But perhaps, based on the fact that your friend heated his second level in this fashion may lend support to the idea that I need more insulation in the attic.

Any more thoughts would be appreciated!

Michael

Logged
HeatMasterSS MF5000E by Yoder Heating
MS 460 Stihl Magnum
Husqvarna 345
8lb Wood Splitter with 'High Performance' Fiberglass Handle
5 acres

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #3 on: October 03, 2011, 03:02:55 PM »

i would suggest that IF you think you don't have enough insulation then you likely don't. anyway if your attic is not 12 or 14 inches thick and you live in a cold winter climate you would be spending money wisely in my opinion (that isn't worth much) and also the grate idea is solid..it would give a place for teh cold air another route to fall and let more heat up the stairwell yousay you allready have. the grate is a cheap to try
Logged
home made OWB (2012)
Ontario Canada

BIGDIESEL20S

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 82
  • OWF Brand: Hardy
  • OWF Model: H-2
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #4 on: October 03, 2011, 08:25:16 PM »

I would do the insulation before I done anything else. With the open stair case and the fact the 2nd story is over the 1st        (heat rises), you should not have that much temp differance in down to up. There will be some but not that much. Most of the time the 2nd story will be a little warmer than the 1st unless you are losing heat and most all heat lost goes up. The best way to tell if you have got enuff insulation in your attic is frost, if your roof will hold frost for a long time into the day you are not losing much heat but if its gone quik or you see spots thats where your heat is leaving. But you have to have a good frost and you cant make a judgement where the sun is hitting the roof.
Or you can also pay through the nose to have somone come to your house with one of those heat seeking radar gun things and walk all over your house to tell you the same thing the frost will tell you.
Logged
2002 F250 SUPER DUTY 4X4
1994 CHEVROLET S-10 4X4
HOME MADE 20 TON SPLITER
STIHL: 009, 011, MS250, 026, MS260, 028 SUPER,  028FARMBOSS, 029 SUPER, 031, 031 SUPER, 066.
176 ACERS HALF WOODS
HOME MADE PICKUP BED TRAILER
801 FORD POWERMASTER
B414 ITERNATIONAL
H FARMALL

rosewood

  • Full Member
  • ***
  • Offline Offline
  • Posts: 201
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #5 on: October 03, 2011, 08:37:38 PM »

not sure where your located,but here in mass if you put a vent in a floor and there was a fire ,insurance co .could refuse coverage cause you create a fire draft thru the floor.something to check into if you go with that option.
Logged

mcarter

  • Full Member
  • ***
  • Offline Offline
  • Posts: 100
  • OWF Brand: HeatMasterSS
  • OWF Model: MF5000e
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #6 on: October 04, 2011, 07:30:04 AM »

Thank you all for the insight.  I will call around to get some estimates for insulation.  I will let you all know if that helps!

Michael

Logged
HeatMasterSS MF5000E by Yoder Heating
MS 460 Stihl Magnum
Husqvarna 345
8lb Wood Splitter with 'High Performance' Fiberglass Handle
5 acres

Airgap

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #7 on: October 04, 2011, 01:05:02 PM »

More insulation is always a good investment.
Logged

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #8 on: October 04, 2011, 08:32:45 PM »

 Good to see you on here, you will find that it is a great place to collect information. Lots of different perspectives.
 One thing you might try is using the heat pump to heat the 2nd story up to the desired temperature and then see how long it takes for it to cool off. If it cools off quickly its a sign of needing more insulation. If it takes a while to cool off it would seem like it may be more of a problem that the air from downstairs just isn't finding its way upstairs. Hooking up a upstairs unit isn't that hard if you can get water lines from the basement to the attic, but if there is no where to run them it can be rather hard.
Logged
Southwest Virginia
WF4000 Heat Master

mcarter

  • Full Member
  • ***
  • Offline Offline
  • Posts: 100
  • OWF Brand: HeatMasterSS
  • OWF Model: MF5000e
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #9 on: October 05, 2011, 09:52:02 AM »

Thanks yoderheating, I've been enjoying my OWB! Been on this site reading all the stuff, even the old posts from way back. I cant seem to satiate my craving for info on these OWBs! It has become a strange obsession. I found some intriguing posts on clothes dryers.

I set the second level thermostat down from 69 to 66. The temp drops quickly to 66, less than an hour.  It must be the attic insulation. My neighbor works for Kent's Insulating and he had insulation blown into his attic that met Minnesota standards, I think 3 feet deep! Im going to have this done to my home. If that doesn't help considerably, I'll call you up for an estimate on an attic hx/air deal.

Thanks,

Michael
Logged
HeatMasterSS MF5000E by Yoder Heating
MS 460 Stihl Magnum
Husqvarna 345
8lb Wood Splitter with 'High Performance' Fiberglass Handle
5 acres

mcarter

  • Full Member
  • ***
  • Offline Offline
  • Posts: 100
  • OWF Brand: HeatMasterSS
  • OWF Model: MF5000e
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #10 on: October 06, 2011, 02:02:49 PM »

Estimate for blown-in attic insulation:

$650 to add R19 factor to existing R19 batt for total R38
$1095 to make a total R60 factor

These are 'installed' estimates.

Any thoughts for the southwest VA area?

Michael
Logged
HeatMasterSS MF5000E by Yoder Heating
MS 460 Stihl Magnum
Husqvarna 345
8lb Wood Splitter with 'High Performance' Fiberglass Handle
5 acres

oldchenowth

  • Guest
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #11 on: October 08, 2011, 06:07:23 AM »

I am not sure how it works in your area, but here in Michigan most places you buy blown in insulation will let you use a blower for free for a day.  I have yet to do my house now, but my last one cost me about $225 for 14" on a 1000sft house and about 3 hours of time with the help of a friend loading the hopper.  Might be worth checking into DIY.  Our Menards ads always have spreadsheet info on how many sft per bag per X" deep = R factor to help figure before you get there to purchase.
Logged

Bull

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 662
  • OWF Brand: Hardy
  • OWF Model: Rebuilt H2
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #12 on: October 08, 2011, 08:50:17 AM »

I just re insulated mine (30 bags) and used the blower for free for about $200 
Logged
Southern Indiana
Just outside of the "Small Town"

Ridgekid

  • Guest
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #13 on: October 08, 2011, 08:55:08 AM »

I did mine last fall and got the machine to blow it in for free. (Home Depot). 23 bags of the pink stuff and a couple of rolls of backed insulation for the stairwell (Attic side was only covered and then blown in over it) For under $500, then Uncle Sam gave me a energy savings tax credit.
Logged

teburman

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
    • View Profile
Re: More attic insulation vs. Adding hx/air to attic unit
« Reply #14 on: October 13, 2011, 09:06:50 AM »

Do you have cold air return vents anywhere upstairs?

I doubt additional insulation would solve your problem as it appears your house was designed to have heat source at both levels. You may have enough capacity from the first floor unit to heat the upstairs but you need a mechanism to get the heat upstairs which by default means you need a way for the cold air from upstairs to get back downstairs.

BTW if you are underinsulated you should add more. Blown in insulation is not very difficult to install.
Logged
It's a good life if you don't weaken.

Bloomingdale - in the Adirondack Mountains of NY.