I have four zones/thermostats. One thermostat is connected to the TT terminals on the aquastat and upon a call for heat will start the oil burner. The other three connect to circulator pumps that are triggered by the other thermostats, but are independent of the oil burner. The aquastat is a R8182D, which I have wired for cold start. The oil heating unit is a Burnham V-15A-T.
I want to run that one thermostat independent of the oil burner. However, I want the oil burner to kick on when the temperature falls below some threshold I determine. For two reasons, sometimes the OWB cannot keep up with the demand and I want the oil burner to provide a little bump. And if for some reason the OWB fails to provide heat, e.g., the fire goes out while I'm away and have someone supposedly filling it, or, whatever.
What aquastat, contact type I presume, would you recommend and how should I wire it. Could I wire it to start the burner at, let's say 115, and remain on to another temperature of my choosing, perhaps 150. I don't think using a low limit only would serve my purpose. That is, if my understanding is accurate, that would allow me to use 115, but with the max differential (25) the high temperature would be 130.
Would one of those Honeywell's that I could wire to the TT terminals work? Or perhaps a Ranco and turn line voltage on/off to the burner, or with a 24V transformer? How would that be connected? There is an OWB loop, HX, and house side loop. Hot water baseboard radiators.
Thanks guys,
Gary