Try opening it manually and flushing it like you would if you were purging air from that zone,at the same time give it a good tap on the valve with a wrench, this may dislodge anything stuck in the valve, the zone valve is normally closed with lack of power so it is not wiring or a bad valve, it is stuck open for whatever reason. it could also be a short in the TT wires, try pulling one wire off at the zone valve relay for that zone and see if it closes, if it does, there is a short somewhere.