Pages: 1 [2]
Author Topic: help sizing pumps  (Read 20554 times)
Sprinter
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
Re: help sizing pumps
« Reply #15 on: January 02, 2014, 03:43:27 PM »
I would go back to each exchanger you have and see what btu or GPM they need. 1" pex is recommended to flow 3.8-7.5gpm, PAP is 5.2-10.4gpm.  1gpm@180 supply & 160 return =10,000btuh.
Just an estimate but pool 200-300kbtu + DHW 40-100kbtu + 2 air handlers 80-120kbtu =320-520kbtuh if all zones are calling. That's a minimum of 32 GPM for 1 tap, this would max out 2" pex. If the boiler only has 2-sets of 1" taps that limits its max btu output to 160kbtuh under safe design.
What boiler model?
Michigan Thumber
muffin
« Reply #16 on: January 20, 2014, 07:43:46 AM »
What boiler model?
CB 6048.  Thought it was rated to 500K BTUs if I remember right.
LittleJohn
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
« Reply #17 on: January 20, 2014, 07:53:49 AM »
If memory serves me correctly the largest port on the 6048 is 1.25" - about 10-12 GPM
cando attitude
  • OWF Model: BL 28-40
« Reply #18 on: February 07, 2014, 07:17:29 PM »
Do yourself a big favor and read this http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf
Great reading for anyone that wants to do things right.
Thanks for posting the link hondaracer.........indeed I found it very informative reading....would highly suggest to others looking for objective information
Echo CS 400
Jonsered 2255
Case 35B
Dirty hands splitter
2013 3500 Duramax
Pages: 1 [2]