Welcome, Guest. Please login or register.
Did you miss your activation email?

Username: Password:

Author Topic: Temp drop on radiant heat  (Read 8861 times)

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Temp drop on radiant heat
« on: February 14, 2014, 09:28:00 PM »

I am currently running a empyre pro 400.  In my barn which is 5000 sq ft I have radiant infloor heat in the slab on the first floor and staple up under the sub floor on the second floor.  When I have more than one large zone call for heat the return temps drop significantly.  My temp can be at 180 and if I have 2 of the larger zones call at the same time the "optimizer" or thermostatic valve will kick in so the temp going back to the boiler won't drop below 140.  I know this is protecting the boiler which is fine but just wondering what I can do to try and prevent this.  I am currently running the boiler at 180 with a 5 degree differential.  I have 1" Logstor feeding the barn.  It is 130 foot run one way from the boiler to the 80 plate heat exchanger exchanger.  I have six zones of heat with the 2 larger zones have 8 loops of approx 280' of 1/2 pex.  I am running a Armstrong 9.2 pump.  The run from the boiler to the house has 1-90 and 6-45 degree bends.

Just wondering if I put a larger pump in would that help or should I just live with it.  It just seems to take a long time for the boiler to recover after this occurs.

Thanks for any help.
Logged
Gilford NH

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Temp drop on radiant heat
« Reply #1 on: February 15, 2014, 05:28:43 AM »

What's the differential for the radiant heat? Maybe try a 1 degree so it doesn't take as long before it shuts that zone back off?
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: Temp drop on radiant heat
« Reply #2 on: February 15, 2014, 06:35:49 AM »

I am using a uponor thermostat made for radiant heat and it has a 1 degree differential.
Logged
Gilford NH

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Temp drop on radiant heat
« Reply #3 on: February 15, 2014, 06:41:42 AM »

Are you changing the temps of the radiant slab, if so leave them at one set point. If the stove manufacturer will allow it, turn the temp up on the stove, I run all my installs at 190 or above.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

ITO

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 254
  • OWF Brand: HS1
  • OWF Model: 555
    • View Profile
Re: Temp drop on radiant heat
« Reply #4 on: February 15, 2014, 06:45:19 AM »

 Can you use a priority zone and have only one loop call at a time or maybe half the loops depending on setup? I use floor/air sensing averaging tstats for my floor zones, they switch often and keep the loops warm so there is less heating, cooling and more consistent temps, it works well for me, not sure if that would help you or not.
 http://tekmarcontrols.com/products.html
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Temp drop on radiant heat
« Reply #5 on: February 15, 2014, 06:48:39 AM »

Great option Ito, where's that like button
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: Temp drop on radiant heat
« Reply #6 on: February 15, 2014, 06:53:53 AM »

I have tried to use the priority but when it is real cold by the time the priority zone is satisfied the other zones are calling.  I spoke to Empyre and they don't want me to run the temp above 180.
Logged
Gilford NH

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: Temp drop on radiant heat
« Reply #7 on: February 15, 2014, 07:21:55 AM »

I looked at the floor/air sensing thermostat.

 http://www.pexsupply.com/Wirsbo-Uponor-A3041501-SetPoint-501s-One-stage-SetPoint-Controller-with-floor-sensor-2068000-p

I think I will try one next year and see how it works.

Thanks
Logged
Gilford NH

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Temp drop on radiant heat
« Reply #8 on: February 16, 2014, 05:13:30 PM »

What do you have for mixing valves and is this just a one pump system?
Logged
Michigan Thumber

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Temp drop on radiant heat
« Reply #9 on: February 16, 2014, 05:31:01 PM »

What do you have for mixing valves and is this just a one pump system?


From the 9.2 pump specs its 40' head max and 38gpm max. Very steep curve. 260' of logstor 1" @ 7gpm is 30'head not including fittings or exchanger.  And above 35' that 9.2 is under 5-6 GPM.
Logged
Michigan Thumber

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Temp drop on radiant heat
« Reply #10 on: February 19, 2014, 09:37:51 AM »

BELKAP, is garage 5000sf total or each level??? 
  Are you runing a mixing valve between the OWB and the inslab? or are you runnign 180f water thru slab?? 
    Only reason I ask is I thought my dealer told me never to run the water temps for inslab over 140f or 150f, potential for excessive cracking and degridation of concrete.

Lets do some math; say you are running at 5gpm and temperature drop of 40f (max drop with out thermostatic kicking in)
BTU= GPMxdTx500   ->  5x40x500 = 100k BTU/hr  -> divided by 5000sf = 20 BTU/sf which is typically what you would want for a typical radiant application

So since you can not increase the temperature drop before returning to OWB, and still need more heat for building; you may need to increase the GPM to get more heat out of OWB. 

NOTE: Most people on this forum (from experience and a bit of reading) typically run in thearea of 20f across loops.

Logged

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Temp drop on radiant heat
« Reply #11 on: February 20, 2014, 08:09:05 AM »

Different radiation requires different delta T.  There are charts and design tabs that show many types.

Infloor is 10 degree for reverse return layout. The more even you want the room comfort or heated the smaller the DT. As long as you build in flexibility, you can dial in what works best for you.
A simple mixing manifold or manifold block will control temp and provide adequate flow. That size should have multiple manifolds, or you would need commercial size $$$$ circ to do 5k on one mani.
Logged
Michigan Thumber