PLEASE, do some more reading before you start, there are several things that will be an issue if you go the route that you are headed. 1st is putting the boiler in the garage, the beauty of an OWB is the reduced risk of fire along with the lack of smoke and mess inside, could you put the boiler outside and next to the garage with proper clearance from combustibles? 2nd is pressurized vs non pressurized, you will need to install a plate exchanger at the boiler in order to pressurize the loop running uphill to your boiler in the house otherwise you will be constantly fighting a battle to keep air out of the system. 3rd is line sizing and quality of product, remember that all North American pipe is sized nominally,( outside measurement ) Logstor is just over 1 inch inside diameter, this will help with flow, Quality of product, you will not find a better pipe on the market than Logstor for heat loss or durability, any joints in the piping or casing will allow water to infiltrate the insolation and destroy it's ability to hold the heat inside the pipe, any moisture inside the casing will wick away your heat to the groundwater!