Author Topic: tell us> set boiler temp / differential / return temps / gf alpha pumps  (Read 8101 times)

atvalaska

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1281
  • OWF Brand: aqua-therm
  • OWF Model: coal one 275
  • 907, no vacancy !
    • View Profile

I just fired my boiler for the 1st time ever on Friday moirn    the "paperwork" said to set the boiler to 180 @ 18 psi and a 10 deg  differential  ...... why ??  I set it to 170 and then the 10 ...and the psi hangs at 20,( both the gauge that came with the boiler and my aximon  boiler tender), thing is when the boiler shuts down after a call for heat the temp climbs to 175 and stays there...  I've had to only add wood 1 time since Friday!   21 to 12 deg outside temps, heating a  4 zone slab in 1200 sqf  shop  (70degs in here is a bit much !)  last call for heat in the shop was Saturday morning at 9am the again last nite at 2am  I have two pumps  both GF one regular 3 speed after my 4 way valve  to run the zones and one the alpha  that pumps from the boiler thru the 4way and back .... I put the alpha pump in auto-adap and it burms 43 watts and pumps 11 gpm ...with no call for heat ........... seems mighty high for a pump just pushing a loop with no calls for heat .... how to go about setting the "speeds" and  what should I be  looking for in return temps (of the water coming back into return ) I have my 4 way set to supply  temps between 85 and 110  on a outdoor reset, my return boiler water at 140
« Last Edit: October 26, 2014, 11:12:38 AM by atvalaska »
Logged

atvalaska

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1281
  • OWF Brand: aqua-therm
  • OWF Model: coal one 275
  • 907, no vacancy !
    • View Profile

very 1st fire

atvalaska

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1281
  • OWF Brand: aqua-therm
  • OWF Model: coal one 275
  • 907, no vacancy !
    • View Profile

;(

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile

ATV - The alpha is pumping crazy fast, because it is such a short loop. Might want to try one of the other setting on the alpha to see if you can slow down the water a bit and still maintain a delta T less than 20f.  Cause if I rememeber you have 1" PEX right, and 11gpm is a bit fast; if you have 1 1/4" -> 11gpm is ok water/pumping-wise.

In regards to your calls for heat, I am not sure of you heat loss; but that seems like a might big boiler for only a 1200 sf slab. 

About the temperture of the boiler rising after a call for heat, that is somewhat normal condition called "overshooting". 
Logged

atvalaska

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1281
  • OWF Brand: aqua-therm
  • OWF Model: coal one 275
  • 907, no vacancy !
    • View Profile

I have  1.25 pex ...120' there&back, the building is only calling for heat 1 or  2 times in a 24hr period  but every time I go look at the pump in auto a dap ..its running 11 gpm ....is my pump on "the short bus " of its leaning curve?  seems to me it should be sleeping  22 hours a day :bash:

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile

OK, might be a dumb question, but does your Alpha run all the time or just when there is a call for heat?

If you are running 100% of the time and you want to reduce the GPM, you may want to try the constant pressure feature of the pump.  They are the three indicating bars to the right of the auto-adapt.
Logged

atvalaska

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1281
  • OWF Brand: aqua-therm
  • OWF Model: coal one 275
  • 907, no vacancy !
    • View Profile

 yes all the time ....is it still learning?.....I put it in auto -a-dap last nite at 7pm ...going to see what that does for it , My 4 way in the shop is set for 85-110 degs on the outdoor reset...I was getting a slug of 120-130 temps at the manifold ,so I moved the sensor things settled down after that and I found that the gf 15/58 3 speed after the valve ,needed to be in the speed 2 spot then the 4way was/could work, well see tonite........I moved my boiler temp to 179 and a diff of 10 ....I seen that moving the diff to much/to low was lowering the psi just enough to have the aximon kick on and bring her up >>>then it would be "to much psi" when she got up to temp

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile

It should not take more than a few minutes for the auto-adapt to "LEARN", as the pump is looking for a balance between power consumption, gpm and pressure.  Somewhere in the circuit board this happens, I guess.

...that being said I have an alpha with a varying load behind it; it can have anywhere from 1-12 loop open, this is where auto-adapt really shines (can go from 1gpm up to about 6gpm, with a swing from 22watts to 42watts).  Basically the auto-adapt features, prevents reduces the potential to over or under pump a system.
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com

Great description LittleJohn! I personally would like to see one with more umpfh,  lets say 5-20 gpm
Logged
Wood boiler sales, service and installation for the Northeastern USA.

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile

Great description LittleJohn! I personally would like to see one with more umpfh,  lets say 5-20 gpm
I agree with Slim, about being awesome  ;D ... and possibly with the bigger SMART pump.

The only concern I would have pushing water over 10gpm, would be velocity issues in the fittings!!!  You don't want to go too fast, and create more issues with water turbulance related leaking, than with not enough heat.
Logged

Sloppy_Snood

  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 511
  • OWF Brand: Portage & Main
  • OWF Model: BL 34-44 Shaker
  • "Welcome to second place." - Steve Conover
    • View Profile
    • Indian Creek Shooting Systems
Re: tell us> set boiler temp / differential / return temps / gf alpha pumps
« Reply #10 on: October 30, 2014, 09:29:43 AM »

Great description LittleJohn! I personally would like to see one with more umpfh,  lets say 5-20 gpm

What pump beyond the Grundfos Alpha possesses the "umph" level (5-20 gpm) you are talking about Slim?  Trying to understand why you are supporting a faster flow rate.  Thank you for any clarifying information.  :thumbup:
Logged
NWP 49mm Short Block-modified Stihl 029 Farm Boss
Harbor Freight 20-ton Dual-Direction Log Splitter
2006 Chevy 2500 3/4-ton 2WD
New Holland TC33D 4WD

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: tell us> set boiler temp / differential / return temps / gf alpha pumps
« Reply #11 on: October 30, 2014, 10:16:22 AM »

Great description LittleJohn! I personally would like to see one with more umpfh,  lets say 5-20 gpm

What pump beyond the Grundfos Alpha possesses the "umph" level (5-20 gpm) you are talking about Slim?  Trying to understand why you are supporting a faster flow rate.  Thank you for any clarifying information.  :thumbup:
He is probably looking for something along the lines of a 26-99, but with the SMART or Auto-adapt feature
Logged

Sloppy_Snood

  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 511
  • OWF Brand: Portage & Main
  • OWF Model: BL 34-44 Shaker
  • "Welcome to second place." - Steve Conover
    • View Profile
    • Indian Creek Shooting Systems
Re: tell us> set boiler temp / differential / return temps / gf alpha pumps
« Reply #12 on: October 30, 2014, 10:18:28 AM »

He is probably looking for something along the lines of a 26-99, but with the SMART or Auto-adapt feature

Thank you Littlejohn.  I am ignorant of pumps really so I ask this: what is the "advantage" of going with a larger pump then?
Logged
NWP 49mm Short Block-modified Stihl 029 Farm Boss
Harbor Freight 20-ton Dual-Direction Log Splitter
2006 Chevy 2500 3/4-ton 2WD
New Holland TC33D 4WD

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: tell us> set boiler temp / differential / return temps / gf alpha pumps
« Reply #13 on: October 30, 2014, 10:23:51 AM »

Sloppy its kind of like why do you put a bigger engine in your car ;D, you want to GO FASTER  :thumbup:.  But in the pump world, "Going Faster" mean either more head pressure or more volume (GPM)

***Just remember, if you overpump (typically water velocities faster than about 5ft/s in a heating system) IT WILL cause damage, start out as excessive noise in the system and eventually erosion of metalic fittings.
Logged

Sloppy_Snood

  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 511
  • OWF Brand: Portage & Main
  • OWF Model: BL 34-44 Shaker
  • "Welcome to second place." - Steve Conover
    • View Profile
    • Indian Creek Shooting Systems
Re: tell us> set boiler temp / differential / return temps / gf alpha pumps
« Reply #14 on: October 30, 2014, 10:25:56 AM »

Thank you LittleJohn.... makes  sense to me.  :thumbup:
Logged