Author Topic: 20 amp breaker keeps tripping  (Read 15861 times)
newmod
  • OWF Brand: HOMEMADE
« on: January 02, 2015, 06:24:22 PM »
I just hooked up and and started the first burn in my new owb.  It is a homemade (2nd one I have built)  taco 009 pump. Ranco aquatat. And normal solenoid for draft door.   Aquastat set at 190 and 160.  Was running fine, up to about 120 deg.  And the 20 amp breaker started tripping.  Only thing on the circuit is the owb with 12-2 wire.  Switched breaker and keeps tripping.  Ran good for about 4 hours without problem now breaker trips in about 3 seconds.  ANY IDEAS OUT THERE ?????.I am gonna take apart the pump totomorrow and see if it has locked up or something.  Also have my buddy (electricalengineer) coming over in the morning.
Newmod
fireboss
Re: 20 amp breaker keeps tripping
« Reply #1 on: January 02, 2015, 06:38:04 PM »
Un plug the pump and you will no rite away if its the pump or not!
newmod
« Reply #2 on: January 02, 2015, 06:56:00 PM »
The pump and aqua state are ran thru a normal switch next to aquastat.  With the breaker off I have the switch off.  Unplugged the solonoid. Switched on the switch and the breaker tripped in a couple seconds.  Maybe the pump locked up for some reason.  I have no idea.  It is such a simple system, I shouldn't have this problem.  Never had any problems with previous build.  Ugh.
newmod
fireboss
« Reply #3 on: January 02, 2015, 07:17:17 PM »
If the switch for the pump is off you have a short perhaps a bare wire touching metal  maybe in the switch box
newmod
« Reply #4 on: January 02, 2015, 07:21:33 PM »
When the switch is off everything is fine and breaker doesn't trip. Once the switch is flipped on it trips in a couple seconds
Jwood
  • OWF Brand: P&M Ultimizer
  • OWF Model: Bl 28-40
« Reply #5 on: January 02, 2015, 07:25:51 PM »
Try a new switch maybe
North Central Minnesota
Stihl MS 270c
Stihl MS 461
Blacked out Fiskars X27
06' Silverado 2500HD Duramax
fireboss
« Reply #6 on: January 02, 2015, 07:33:15 PM »
SO you no its good from the breaker to the switch then  try un hooking the pump and if it doesn't trip the breaker then you no its the pump!
newmod
« Reply #7 on: January 02, 2015, 07:34:46 PM »
Ya. I am gonna just wire nut everything together in the morning.  And then pinpoint it that way.  Gonna disconnect 1 at a time to find the problem.  That pump only draws about 5 amps. So it shouldn't  be that unless jammed or a short somewhere.  I will let you all know what I find in the morning.  Hope it is a simple fix.  It's gonna get real cold here and the freestanding  stove ain't gonna cut it.
fireboss
« Reply #8 on: January 02, 2015, 07:38:25 PM »
Good luck ! That's why most of us keep a extra pump on the shelf they always go out on on the coldest nights and nothing is open!
Jwood
« Reply #9 on: January 02, 2015, 07:41:48 PM »
I have a spare Alpha for that reason also.
Stihl MS 270c
Stihl MS 461
Shrek1112
  • OWF Brand: Hawken Energy
  • OWF Model: HE-2100
« Reply #10 on: January 02, 2015, 07:50:07 PM »
I think Fireboss hit the nail on the head.  When I installed my Hawken the breaker kept tripping. Troubleshooting revealed a wire in the service light was pinched from the factory.  Quick and easy fix, double check to make sure your switch is not wired incorrectly also.
Stihl MS-250
Stihl MS-391
Huskee 35 Ton
Chevy 1500 Crew
13 & 15 year old work force
« Reply #11 on: January 02, 2015, 10:02:17 PM »
The Grundfoss 26-99 only pulls 1.8 amps and that is a hell of a pump, are you sure about the five amps part?
Maybe go the other way, unhook everything and hook em up one at a time?
« Reply #12 on: January 03, 2015, 02:30:19 AM »
Don't rule out that the breaker may be faulty.  Just because it's new doesn't mean it ain't bad... Good luck.  Roger
« Reply #13 on: January 03, 2015, 04:15:00 AM »
Mlappin is right on the Amp draw on the 26-99, unless you are running a commercial pump for industrial use then your Amp draw will be less that 2 Amps, I would bet that it is either a short or if you have a blower such as on a hot air unit that is getting hot and pulling lots of Amps, They are typically drawing 5-6 Amps but when they get hot, the Amp draw will skyrocket, They also should have a thermal overload that shuts them down when they get hot!
newmod
« Reply #14 on: January 03, 2015, 07:49:35 AM »
Ok guys, we figured it out.  The pump and solenoid is only drawing 1.8 amps. No problem.  Pulled the wired off the solenoid. Still tripped.  Pulled the solenoid wire out of the aquastat. Didnt trip.  Installed a temporary hot wire from aquastat. Everything works fine.  IT WAS A BAD WIRE. UGH.  .   Cheap and simple fix.  Just glad I dont have to wait a week to get it in the mail.  The wife is happy now..   thanks guys
Newmod