I took my copper out of basement and replaced it with pex and used pipe straps to hang it ! Doesn't look all that bad! I thought I was having flow restrictions but it didn't make a difference what a waste of money! This year I switched my 40 plate heat exchanger for a 100 plate and see no difference! I guess the only thing left is a bigger pump!!
Iam only 14' away from my house and a nother 10' in the basement I used the 25' on the therm pex the came with boiler when I got it , and got the 10' uninsulated pex from them and put pipe rap around it in basement! my chief complaint is when the temps got down to close to zero , my boiler is at 195 - 185 and my hot water base board is 165 to 170 ! And my house is 65 to 68. Witch we could live with, but when its like 15 above the house can get up to 74 i have a big enough stove to handle the load just cant get it across my now 100 plate exchanger! My temp on my oil burner only still only gets to 170! When I switch to oil its goes up to 180!
With such a short run you could gain some flow with a larger pump but the velocity will get pretty high. You should be around 8gpm right now but that is assuming only 70-80' of 1" pex in the loop. If you have any pex elbows or a lot of other fittings it will drop off from that fast.If you try a larger pump, I would go with a Grundfos 26-99 and put in series with the 007. Then wire it to only come with the thermostat in the house. Also put a manual switch on it so you can turn it off when the house is heating ok with just the 007.