Author Topic: second thermostat won't run blower fan on oil furnace  (Read 136 times)

wonderwhy?

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 9
  • OWF Brand: Hardy
  • OWF Model: H-4
    • View Profile
second thermostat won't run blower fan on oil furnace
« on: October 31, 2019, 07:00:38 PM »

I have my OWB installed, Everything works just as it should with the exception of the fan in my oil furnace wont come on with the second thermostat.  I have read 30+ posts from all different OWB websites. Lots of info out there, I have tried many different things to get it to run the fan.  Right now the only way i can turn on the fan with the second thermostat is to take the face off the thermostat and jump a wire from W to RC.  I ran a jumper back up to G on first thermostat and fan only works on first thermostat.  Is this because I have a delay on the fan for the oil furnace? is it waiting for heat build up?  I am currently burning a Hardy H4 i picked up used, aquastat controls the furnace and i run my pump all the time to keep hot water flowing. Any help would be great.  Thanks Paul  :bash:
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3029
  • OWF Brand: HeatMaster
  • OWF Model: G200
    • View Profile
    • RSI
Re: second thermostat won't run blower fan on oil furnace
« Reply #1 on: October 31, 2019, 09:38:15 PM »

Does the 2nd thermostat run on batteries? If not, do you have a C wire hooked to it?
What terminals do you have the wires on. You should have the wire that used to be on the G terminal in the original thermostat connected to the W in the new thermostat.
You also need a wire added from the RH on the original thermostat(or R if no RH) to the RH in the new thermostat.
Logged

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 351
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
    • www.heatmasterfurnace.com
Re: second thermostat won't run blower fan on oil furnace
« Reply #2 on: November 01, 2019, 04:56:31 AM »

If RC to W works than you  have power to RC. You need a jumper to RH to RC and it should work, battery or otherwise powered. But as RSI said you need C to common if t-stat is powered by 24v from furnace.
Logged
Retiring HeatMaster Distributor for southeast US
 Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

wonderwhy?

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 9
  • OWF Brand: Hardy
  • OWF Model: H-4
    • View Profile
Re: second thermostat won't run blower fan on oil furnace
« Reply #3 on: November 01, 2019, 07:11:00 AM »

I have batteries, that took care of my problem.  I just didn't understand.  The way that i read how to hook the second thermostat up was jumper wire for both R (blue wire) and RC (red wire, 24vac) from thermostat 1 to thermostat 2.  Green wire removed from thermostat one and put in W hole in thermostat 2.  this was a no go for me, no fan.  After taking jumper off of R and using supplied little metal jumper from R to RC i have a fan when second thermostat calls for heat.  So thankful for the quick replies.  I have two identical honeywell thermostats model number RTH111B1016 they do not have the option C some refer too.  Hopefully this will help some poor sucker like me one day.  Thanks again to those that replied over night to help me.

     So this is how i understand my second thermostat now, power comes in on RC is jumped to R using supplied metal jumper that came with honeywell thermostat.  When heat is called for power goes from R to W, done by thermostat automatically controlling the fan in my oil furnace that i hope doesn't burn any more oil.
« Last Edit: November 01, 2019, 07:23:04 AM by wonderwhy? »
Logged

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 351
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
    • www.heatmasterfurnace.com
Re: second thermostat won't run blower fan on oil furnace
« Reply #4 on: November 01, 2019, 07:52:28 AM »

you got it!