Now, I have noticed that the ground where my line is buried from the OWB to the rear of the house is damp.
Lugnnut
I hate to say it but I think you have just found where your wood is going. Check your heat loss between the boiler and house. 3-4 degrees doesn't sound like a lot but is HUGE. More than 5 and your going to be in trouble when we get some real winter weather.
So in essence what you are saying is that my line is not deep enough into the ground? I've read numerous posts on here as well as the arbonist site that read one does not need to put the line down any further than 2'. When others have said to bury it below frost line, what is the frost line? In some areas it is 4', in other area it is deeper or shallower.
Okay, so if I have to dig the pex line up again come spring....anyone see any problem with tying new pex in to the existing line? this stuff was expensive and I don't fathom the idea of going out and spending $1200.00 again for another 200' of line.
Lugnut
[/quote]
If you have good insulation it doesn't matter how deep or shallow it is. Put it in deep and you have a good chance of getting into the water table. Bury it shallow and it may be buried at frost depth. If you are losing heat to the ground why would you put new pex in the existing line? The problem is the lack of insulation not the pex lines. You need to start by getting some real numbers on your heat loss (if any) to the ground. Then you can at least rule things out or start addressing them. If the problem is in the lines you have 3 options 1.Plan on using a crap ton of wood. 2.Spend the money on logstor. 3.Somehow dig up your lines and have them spray foamed with closed cell urethane.